    Post

    If a new service is upgraded 100 amp fuses to 100 amp breakers
    are arc fault breakers required when there was none in the original installation?
    I know that the bedrooms must be protected with arcfault breakers in a new building (no problem) but with a older building separating circuit may involve a lot of extra work ,so if it is required when upgrading to breakers then I should price accordingly.
    thanks for the help,I really appreciate it

  2. #2
    Inactive Member Cosimo Diano's Avatar
    Join Date
    March 27th, 2004
    Posts
    36
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    You do not need to install arc fault breakers if they were not installed in the first place.

  3. #3
    Inactive Member Cosimo Diano's Avatar
    Join Date
    March 27th, 2004
    Posts
    36
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Let me make it clearer. If the permit for the wiring of the bedroom receptacles is dated for April 25, 2002 or earlier, arc fault protection would not be required.

  4. #4
    Inactive Member pilot's Avatar
    Join Date
    May 3rd, 2004
    Posts
    45
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    THANKS COSIMO
    that clears things up for me